F220 Series Detectors with F220-B6RS Bases Install the Bases | en 17
Bosch Security Systems, Inc. Installation Manual F.01U.029.847 | -01 | 2007.02
3.5 Wire Power Supervision Modules
3.5.1 Wire F220-B6E Power Supervision Base
The F220-B6E base is wired as shown in Figure 3.4 on page 18.
1. Positive (+) and negative
(-) resettable auxiliary
power either in parallel
originating from the same
power supply or run from
separate power supplies.
2. Positive (+) and negative
(-) initiating device circuit
(IDC) from the control
panel or an existing
circuit.
3. Interconnection circuit
(connects Terminal 3 from
base to base) for up to five
bases on a common power
supply circuit. Each power
circuit must be terminated
with an F220-B6E Power
Supervision Base or a
D275 Power Supervision
Module.
4. When connecting a D275,
connect the positive (+)
wire to the yellow input
(24 VDC) and the negative
(-) wire to Common
(black). The red wire is
not used.
5. The blue wires from the
D275 Power Supervision
Module provide power
supervision.
6. An EOL resistor as
specified in the control
panel’s installation
instructions.
F ig. 3.3 Interconnection Wiring
Wire Size Wire Length
18 AWG (1.2 mm) 300 ft (91 m)
16 AWG (1.5 mm) 450 ft (137 m)
14 AWG (1.8 mm) 750 ft (229 m)
Table 3.3 Maximum Distance from First to Last Interconnected Units
i
NOTE! To ensure interconnected units can alarm, the line
load after the last detector must not exceed 10 mA.
F01U029847-01.book Page 17 Thursday, March 1, 2007 9:27 AM