8 en | Install the Bases F220 Series Detectors with F220-B6RS Bases
F.01U.029.847 | -01 | 2007.02 Installation Manual Bosch Security Systems, Inc.
2.3.2 Base Specifications
2.3.3 Detector Specifications
2.4 Electrical Supervision
When the F220-B6RS Bases are wired according to the
instructions in this document, the control panel initiates a
trouble signal when a detector is removed from its base,
providing tamper protection. An EOL power supervision
module, such as a D275 or an F220-B6E Power Supervision
Base and an EOL resistor as specified by the control panel
manufacturer, supervises power.
3 Install the Bases
3.1 Mount the Bases
With the exception of the F220-B6E base, all four-wire bases
can be used in any combination within a loop. One F220-B6E
Alarm Current (only base current, detector current excluded)
F220-B6RS (with
steady sounder and
relay):
45 mA at 24 VDC
50 mA maximum at 30 VDC
F220-B6RS (with
separately powered
sounder only):
30 mA at 24 VDC
35 mA maximum at 30 VDC
NAC Current 30 mA at 24 VDC
Standby Current 10 mA maximum at 30 VDC
Voltage 10.0 VDC to 30.0 VDC
Table 2.4 F220-B6RS Detector Base Specifications
Current
Alarm: 35 mA maximum at 32 VDC
Standby: 0.12 mA maximum
Startup: 0.12 mA maximum
Powerup Time 22 second maximum
Rate of Rise
F220-135: 15°F/min (9°C/min) or greater
Table 2.5 F220 Series Detector Heads Specifications